Electricians revenge
1 members (Scott35), 36 guests, and 8 robots.
Page 4 of 4 1 2 3 4
#94279 07/26/05 09:19 AM
250.104(A)(1) has nothing to do with "other metal piping". That requirement is found in 250.104(B).
Ryan Jackson,
Salt Lake City
#94280 07/26/05 10:05 PM
George, I guess the right size ground would be #12 if the circuit likely to energize the pipes is the bathroom lighting or GFCI, and #10 if it was the dryer in the laundry. Kind of a judgement call, is it?
#94281 07/27/05 06:07 AM
I think because this house has 200A service supplied by 4/0 aluminum that we need a #4 copper that jumps all the water piping and returns to the service ground.
#94282 07/27/05 06:18 AM
Matt, I think you need to look up the difference between grounding the water piping against becoming accidentally energized and using a metal water pipe feed AS A PART OF YOUR GROUNDING ELECTRODE SYSTEM.
As you can see from my posts, I am no code whiz, but am enjoying the learning process going on here.
With some of the commercial buildings (malls) I am working on it seems like sometimes I can build my whole service in less time than I can figure out and install the proper grounding---sprinkler, water, bldg steel---which may involve running to the high up steel above, getting out thru the masonry to grd rods, etc.
#94283 07/27/05 06:28 AM
Poorboy, 250.104(A)(1) refers to table 250.66 for sizing the bonding jumper; because this is water piping, 250.104(A)(1) is the only section that applies.
#94284 07/27/05 05:26 PM
So in my earlier reference to the multiple occupancy retirement building, according to 250.104(A)(2) I would use #8 copper (as per table 250.122) because the sub panels in the apts. were 100A. Am I getting any smarter at all?