Im new to posting but have been reading all the forums for a while great stuff!
On to my question we are setting up some panning machines with 1hp motors they are on a 20amp branch circuit with a fused disconnect do I need a overload protection starter as well or just a magnetic contactor? Your replies are appreciated
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
If these motors are single phase, they may have built in overload protection, read the data plate.
If these are 3 phase motors, then it is unlikely that they will have overload protection & you will have to supply it.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
The NEC requires all motors to have some sort of overload protection.
That may well be already provided in the motor or it may not be, as Tom stated.
Take a look at 430.32(B) or 430.32(D) depending on if the motors are automatically started or not.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
IBM used a buttload of 3p motors in their equipment and they all had O/L protection in the motor but you do have to read it on the nameplate to believe it.
Greg Fretwell
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
Aren't those little clicks- on overload protectors that come on three phase AC compressors used for other purposes besides AC/ Reefer motors?
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Don't forget about the possibility of an impedance protected motor or the fact that sometimes the Short Circuit and Ground Fault device can also serve as the overload device per 430.55
George Little
|
|
|
|
Joined: Aug 2005
Posts: 1
Junior Member
|
you should know that most starters and motors have a variety of ways to be wired what exact type is your starter and motor
|
|
|
Posts: 404