#93731 06/08/05 06:29 PM
Joined: Mar 2004
Posts: 16
J
JG Offline OP
Member
Would it be permissible to use sch 80 in a hospital, with two grounds as long as you did not supply patient areas or emergency power through it?(You would still use a mettallic raceway for these areas)

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93732 06/08/05 09:56 PM
Joined: May 2005
Posts: 16
T
Member
I don't think that you can use PVC in a hospital under any circumstance. I have never seen PVC in the hospital that I worked in.

#93733 06/09/05 08:07 AM
Joined: Mar 2003
Posts: 849
Y
Member
517.13 a wiring methods,
517.30c(3) Exceptions 3& 4 Essential Electrical Systems

#93734 06/09/05 10:00 AM
Joined: May 2002
Posts: 1,716
R
Member
JG, there is no need to put two EGC's in PVC in a hospital.

In the applications where PVC can be used in a hospital, there would be no reqirement for this to be done.

See Yoopersups' code references, as well as 517.12


Roger



[This message has been edited by Roger (edited 06-09-2005).]