#93529 05/30/05 04:36 PM
Sorry to bring this subject up again, but I searched the some of the archives, and didn't see a definite answer about the master bedroom lights having to be on the bedroom AFCI circuit. I may have missed it though. In my opinion it would be best, but is it required? I don't seem to see it "spelled out" in the code. It only says bedroom outlets.... Thanks Steve... Also how about the master bedroom closet light? I would think so. Steve
[This message has been edited by sparkync (edited 05-30-2005).]
#93530 05/30/05 05:14 PM
The consensus seems to be that a ceiling box is an outlet as defined in the code. So is a receptacle, smoke detector etc. because they are "a point on the wiring system at which current is taken to supply utilization equipment"-NEC 2002 Art. 100-Outlets. Thus a box containing just a switch would not be an outlet because it is only for control, not utilization.
#93531 05/30/05 05:59 PM
Greg, I'm actually talking about the switch not necessarily being in the bedroom, but the switch in the bathroom controlling the lights. I know technically, by "wording" that the bathroom is not the bedroom, but looks to me like they would still be considered one. If an arch originates in the bathroom lighting next to the bedroom, would not the same hazard be present when the homeowner is asleep, being it is so close to the bedroom? I know according to the wording that it wouldn't have to be, but it don't make a lot of sense to me. Thanks again.. Steve..
#93532 05/30/05 06:35 PM
There's no reason you can't go beyond the minimum of the code if you wish. If the light that is being controlled is in the bedroom then that circuit must be AFCI protected. The decision is based on where the "outlet" is, not the switch that controls it. Frankly I think that the whole AFCI thing is a solution looking for a problem anyway.
#93533 05/30/05 07:17 PM
Greg, I agree.. Somethings just don't make right good sense..Steve
#93534 05/30/05 08:01 PM
It also depends on which NEC version you're under. The '99 says bedroom receptacles only, while the '02 calls for all utilization points in the bedroom, even smokes, but does not appear to include closets.
From the 1999 NEC:
210-12. Arc-Fault Circuit-Interrupter Protection.
(a) Definition.
An arc-fault circuit interrupter is a device intended to provide protection from the effects of arc faults by recognizing characteristics unique to arcing and by functioning to de-energize the circuit when an arc fault is detected.
(b) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere receptacle outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter(s). This requirement shall become effective January 1, 2002.
From the 2002 NEC:
210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Definition.
(B) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt, single-phase, 15- and 20-ampere outlets installed in dwelling unit bedrooms shall be protected by an arc-fault circuit interrupter listed to provide protection of the entire branch circuit.
[This message has been edited by Larry Fine (edited 05-30-2005).]
Larry Fine
Fine Electric Co.
fineelectricco.com
#93535 05/30/05 08:23 PM
Lest we open old arguments.....a switch is not an outlet- so a switch in the bedroom controlling a light in the bathroom need not be afci protected. A switch outside the bedroom that controlled the bedrom would require such protection.
#93536 06/05/05 01:17 AM
why is a switch not an outlet?
Outlet. A point on the wiring system at which current is taken to supply utilization equipment. (2002)
#93537 06/05/05 01:36 AM
Joe,
A switch is not an outlet, because the ultilization equipment is not installed at the switch.
Don
#93538 06/05/05 09:36 AM
In my opinion we have to accept Don's interpretation of outlet. [Linked Image]
If we did say that a switch is an outlet than almost everything we install becomes an outlet.