Since we are required to use conductors suitable as sunlight resistant, are the conductors inside SEU cable meeting that requirement and usable as a cable riser for Service Entrance conductors? Must it say "Sunlight Reasistant" on the conductors?
George Little
#93374 05/19/05 09:02 PM
Page 40 UL Wire and Cable Marking Guide
SERVICE ENTRANCE CABLE (TYLZ)
GENERAL
This category covers service entrance cable designated Type SE and Type USE for use in
accordance with Article 338 of ANSI/NFPA 70, “National Electrical Code” (NEC).
Service entrance cable, rated 600 V, is Listed in sizes 14 AWG and larger for copper, and 12 AWG and larger for aluminum or copper-clad aluminum. Type SE cable contains Type RHW, RHW-2, XHHW, XHHW-2, THWN or THWN-2 conductors. Type USE cable contains conductors with insulation
equivalent to RHW or XHHW. Type USE-2 contains insulation equivalent to RHW-2 or XHHW-2 and is rated 90°C wet or dry.
The cable is designated as follows:
Type SE — Indicates cable for aboveground installation. Both the individual insulated conductors and the outer jacket or finish of Type SE are suitable for use where exposed to sun.
Types USE and USE-2 — Indicates cable for underground installation including direct burial in the earth. Cable in sizes 4/0 AWG and smaller and having all conductors insulated is suitable for all of the
underground uses for which Type UF cable is permitted by the NEC. Types USE and USE-2 are not suitable for use in premises or aboveground except to terminate at the service equipment or metering equipment.
Both the insulation and the outer covering, when used, on single and multiconductor Types
USE and USE-2, are suitable for use where exposed to sun.
#93375 05/19/05 11:03 PM
Thanks Joe.
George Little