ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 546 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#93265 05/15/05 07:00 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
George with the proper use of isolation modules even a short in the addressable loop can be worked around with a class A system.

The majority of systems I install are fully class A. [Linked Image] Few get the isolation modules. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93266 05/15/05 10:13 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
The difference between a Class A Style 6 and Class A Style 7 is the isolation modules and the associated ability to operate under a fault.
I specify in most cases, a hybrid Style 6/7 which has a style 6 circuit, with an isolation module between each control panel and every 10 device on the SLC loop.


Ron
#93267 05/15/05 12:26 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Can You T-tap with an addressable system? Code reference please [Linked Image]

[This message has been edited by George Little (edited 05-15-2005).]


George Little
#93268 05/15/05 03:40 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
A class 'B' addressable SLC loop can be T-taped per minimum code.
A class 'A' loop could not because there wouldn't be a supply and return loop.
NFPA 72-2002 6.4.2.1

Most of the time, when I specify a class B circuit, I also specify no T-taps to ease the future troubleshooting burdens.

[This message has been edited by Ron (edited 05-15-2005).]


Ron
#93269 05/15/05 04:30 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Thanks Ron. I'm not the sharpest tool in the shed when it comes to Fire Alarms plus, I don't have a copy of NFPA 72.


George Little
#93270 05/15/05 07:07 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Unfortunately there are requirements in the Building Code, NFPA standards 13, 70, 72 and 101.
I get challenged pretty often with code related questions and struggle often.

I'm working on one now that is hard to put my finger on the answer. An inspector has stated that he wants smoke detectors and sprinklers below a computer room raised floor. Although I think I've got the ammunition needed, it isn't a slam dunk and always need to search through the code to find more.


Ron