ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Electricians revenge
by gfretwell - 05/09/24 08:24 PM
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 152 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#93231 07/03/05 01:11 PM
Joined: Jul 2005
Posts: 56
P
Member
NESC do not require handhole covers to be bonded.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93232 07/03/05 05:17 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Paul,
Most of the questions on this site involve electrical contractors who are subject to the NEC, not the NESC, and the NEC requires this bonding. Based on the number of deaths and injuries caused each year by unbonded covers in installations under the NESC, it is my opinion that the NESC should be changed to protect the public.
Don

edited to add missing words

[This message has been edited by resqcapt19 (edited 07-03-2005).]


Don(resqcapt19)
#93233 07/03/05 09:20 PM
Joined: Mar 2003
Posts: 849
Y
Member
Handhole, When you put up a pole theres a Handhole Right. The pole is bonded. Is the Cover?? (No) Handholes in the Ground Every one I;ve seen to date have been nonconductive with covers of the same so bonding has not been an Issue. Anyone whos been in any amount of manholes (Larger) knows theres usually a Grounding buss. There usually concrete and openings about 7ft 6 inches to 8ft up. Since deregulation I;ve worked on a LOT of 13.8 -4160 ect so its in the realm of the Electrical contractor.I have never seen a Manhole cover Grounded or seen a Kit to ground one.

#93234 08/06/05 01:18 PM
Joined: Jul 2005
Posts: 56
P
Member
I agree with the fact there is no requirement in the NEC or the NESC of bonding the Manhole Cover. On the DOE project I am on the DOE does not come up with Code arguments but come up with incidents where because the action was not taken an incident happened. Our solution to this was to bond the ring of the manhole itself thus providing a bond between the ring and the cover caused by the weight of the cover. BTW there is no requirement either in the code requiring the bonding of Vault or Substation doors.

#93235 08/06/05 02:53 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Paul,
Quote
I agree with the fact there is no requirement in the NEC or the NESC of bonding the Manhole Cover.
250.4(A)(3)requires this bonding.
Don


Don(resqcapt19)
Page 2 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5