ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 523 guests, and 35 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#93060 04/28/05 02:08 PM
Joined: Apr 2005
Posts: 73
D
dlhoule Offline OP
Member
My facility recently replaced a hot water heater. This is a 3 phase 440 Volt heater.
The original water supply to this heater was galvenized pipe. It has been replaced with plastic. I am of the opinion that it would be a lot safer to pull in a ground wire, rather than rely on conduit for grounding. This conduit has been there for over 30 years and we have had several roof leaks with conduit getting wet and corroded. What would be your recommendations for this?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93061 04/29/05 11:39 AM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Welcome to ECN.
Our 'standard' practice is to "pull a ground".

Also, don't forget to 'jump' the metalic hot and cold water lines, as you may have 'lost' the grd bond with the replacement htr.

John


John
#93062 04/30/05 05:43 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
don't forget to 'jump' the metallic hot and cold water lines

While this is never a bad thing to do there is no specific requirement in the NEC to do so. [Linked Image]

The metal water piping systems are required to be bonded however there is no reason that must happen at the water heater or that a bonding conductor must be installed.

The hot and cold water pipes are very likely to already be bonded together at tub and shower valves, laundry valves, mixing valves at the boiler etc.

If we say those are not reliable connections we might as well put a bonding jumper around every soldered connection.

For what it's worth here is the 2002 Handbook commentary.

Quote
If it cannot reasonably be concluded that the hot and cold water pipes are reliably interconnected, an electrical bonding jumper is required to ensure that this connection is made. Some judgment must be exercised for each installation. The special installation requirements provided in 250.64(A), (B), and (E) also apply to the water piping bonding jumper.

Hey John I am not picking on you here, this is just a pet peeve of mine when I see inspectors say the hot and cold must be bonded at the water heater.


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#93063 04/30/05 06:37 AM
Joined: Apr 2005
Posts: 73
D
dlhoule Offline OP
Member
Thanks John & Iwire, just a point of info. This heater is for shower facilities. Original was installed in the sixties at which time there were no requirements for the hot & cold water lines to be bonded together. In this case I think it is an excellent idea. We now have plastic supplying the heater and galvenized running to the shower and lavatory facilities. John, when you say pulling a ground is standard practice in your area, are you referring to replacement of existing equipment, new equipment or both?

#93064 05/01/05 08:35 AM
Joined: Feb 2002
Posts: 2,233
H
Member
Bob,

I agree with you that the hot and cold water must be bonded together but not at the water heater. If I was inspecting a job and I don't see the jumper wire at the water heater, I would try to look at a boiler or washing machine to see if there is a connection between the two. However for the $5-$7 dollers worth of parts for the bonding wire and clamps, most guys just throw it on. Also if the bonding jumper isn't at the water heater and it is bonded elsewhere, sometimes it is hard to find out where it is bonded. Some AHJ's might not take the extra time to try and find out where it is bonded.