ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#93038 04/26/05 08:31 PM
Joined: Jun 2001
Posts: 32
G
GEC-1 Offline OP
Member
I cannot find the code article that states that the grounded and grounding conductors may be joined only at the disconnecting means. Can someone help?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93039 04/26/05 10:04 PM
Joined: Jan 2004
Posts: 1,507
G
Member
250.142 kinda says that, At least the concept is there.


George Little
#93040 04/26/05 10:24 PM
Joined: Jun 2001
Posts: 32
G
GEC-1 Offline OP
Member
Thanks George! I have a friens that is a home inspector who wanted the info.

#93041 04/27/05 07:49 AM
Joined: Sep 2003
Posts: 650
W
Member
How about 250.24(5) 'Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.' The FPN points out ranges and dryers, SDS and detached structures.

-Jon

#93042 05/01/05 02:07 PM
Joined: Feb 2001
Posts: 308
S
Member
250.24(1) says the connection shall be made at any accessible point from the load end of the service drop or lateral to the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.

You do not have to make the connection at the disconnect, it could be made at the weatherhead, meter or any other point as long as it is accessible and is before the service disco.

#93043 05/02/05 12:32 PM
Joined: Mar 2005
Posts: 399
A
Member
Sorry Steve,
The BOND between the groundED and groundING must be done IN the service disconnect enclosure.
Before anyone gets mis lead 250.24(A)(1)...connection...made at any accessible point...etc. is refering to the connection of the grounding electrode conductor.
250.24(A)(5)prohibits the connection on the load side of the service disconnect.
250.24(B) & (C) list where the bond between the grounded and grounding is to be done.
It must be done IN the service disconnect enclosure.
Alan--


Alan--
If it was easy, anyone could do it.
#93044 05/02/05 10:36 PM
Joined: Feb 2001
Posts: 308
S
Member
Alan,

250.24(A) says "A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5)."

This section deals with the connection between the grounding electrode conductor and the grounded service conductor, not the connection between the grounding electrode conductor and the grounding electrode.

@50.24(A)(1) says "The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means."

This means you can connect the grounding electrode conductor the grounded service conductor at any point from where you make the connection to the utility to the service disconnecting means as long as it is accessible.

To put it in practical terms, are you saying it would not be allowed to connect the cold water ground to the neutral in the metersocket where there are multiple meters and multiple service enclosures? I believe the code would definitely allow this.

#93045 05/02/05 11:08 PM
Joined: Feb 2001
Posts: 308
S
Member
I have read the post again and realize why Alan answered the way he did. The initial question is not clear as to whether it is the grounding electrode conductor or the equipment grounding conductor.

But I think (maybe not hard enough) that you are referring to the equipment grounding conductor Alan, which is not applicable to the sections you quoted.

250.130 talks about equipment grounding conductor connections and all it says in 250.130(A) is that the connection shall be made by bonding the equipment grounding conductor to the grounded service conductor and the grounding electrode conductor.

It doesn't really specify where this must happen.

#93046 05/02/05 11:19 PM
Joined: Feb 2001
Posts: 308
S
Member
Also,

250.24(B) refers to the connection between the grounded conductor and the service enclosure(s)

250.24(C) says the grounding electrode conductor must connect the equipment grounding conductors, the service enclosures, and the grounded conductor to the grounding electrode.

Neither of these sections refer to where the grounding and grounded connections must be made.

#93047 05/03/05 09:44 AM
Joined: Feb 2005
Posts: 693
L
Member
Around here, we're not allowed to run anything into the meter base (I guess because it's POCO sealed) except the service cable. It would be great if we could connect the grounding electrode conductor here, because it's already outside.

Oh, well.


Larry Fine