#93048 05/03/05 11:13 AM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
In Sw Fla the GEC is connected in the meter socket as often as it gets to the service disconnect. The grounded conductor is bonded to the meter can, beyond our control and if you also bond in the service disconnect the standard rule around here is there can be no parallel metal paths between the meter base and the service disconnect.


Greg Fretwell
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93049 05/03/05 06:04 PM
Joined: Dec 2003
Posts: 751
E
Member
Section 250.28 requires a main bonding jumper to be installed. Article 100 defines the main bonding jumper as the connection between the grounded conductor and the equipment grounding conductor at the service.
This tells us that this connection must be made in service equipment only, and this is usually accomplished in the main service panel or main service disconnect enclosure.


Earl
#93050 05/03/05 09:52 PM
Joined: Feb 2001
Posts: 308
S
Member
So in the case where there is a metal raceway riser and a nonmetallic nipple between the metersocket and the panel to prevent objectionable current, it is an illegal installation because the equpiment grounding conductor(riser) is connected to the grounded conductor ahead of the service disconnect?