|
1 members (Scott35),
406
guests, and
8
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Mar 2005
Posts: 212
OP
Member
|
Can somebody help me find a code citation that prohibits the dimming of receptacles in a dwelling? I seem to recall a thread from a short time back, but I can't find it.
|
|
|
|
Joined: Feb 2003
Posts: 687
Member
|
I can't help you with the code referance. I do have a solution.
Lutron has special Rec and cord caps for dimming use. The cord cap is slightly different but will work in any outlet. The dimming rec has a smaller size terminal and a rejection bump. No other cord cap fit it.
Call for prices first. List price seems high. They claim to be the only maker of such a thing.
Tom
|
|
|
|
Joined: Feb 2004
Posts: 133
Member
|
|
|
|
|
Joined: Feb 2004
Posts: 133
Member
|
Oh, the code reference: 404.14(E)
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Active one I just inspected a home with this Lutron dimming receptacle device installed. While it is a Listed device it doesn't satisfy the requirement for receptacles in the wall space. I gave the contractor an option of changing to a "standard" receptacle or adding a "standard" receptacle. He added a standard receptacle.
George Little
|
|
|
|
Joined: Mar 2005
Posts: 212
OP
Member
|
OK, so it's not that I can't dim a receptacle, just that the dimmer must be rated or listed for that purpose. What I actually want to do is dim cabinet lights that have a X-FMR mounted above a cabinet, so the recep isn't a convenience recep in the first place. The lutron recep sounds like a good idea anyway.
|
|
|
|
Joined: Feb 2003
Posts: 687
Member
|
Gregtayler,
Lutron makes 2 versions. A split version with 1 regular & 1 special dimmer rec. The other one both sides of the duplex are made for the special dimmer plug.
If they had the split version (with one side normal) wouldn't that satisfy the wall spacing.
For a fixed cabinet a wip fed transformer might be cheaper and easier.
Tom
|
|
|
|
Joined: Jul 2004
Posts: 625
Member
|
An interesting thing about that Lutron recept is that, while it has a ground contact, it doesn't appear that there exist any plugs with a ground pin that will actually mate with the recept--their plugs are two-pronged. Unless I missed one somewhere.
|
|
|
|
Joined: Jul 2002
Posts: 103
Member
|
There have been issues applying dimmers to general use receptacles since you cannot predict what will be plugged into it later on. Some appliances react very poorly to receiving a solid state dimmer output!! Likewise, the system you are trying to connect MUST be rated for connection to a dimmer and may specify the correct device(s) to use. Certain dimmers are NOT rated to operate magnetic devices such as transformers. Be careful!!
|
|
|
|
Joined: Feb 2003
Posts: 198
Member
|
Gregtaylor,- If you can hard wire this transformer,OK, If not just make the recep a single one.
Shoot first, apologize later.....maybe
|
|
|
Posts: 75
Joined: June 2012
|
|
|
|
|