Generator remote from building ,has disconnect switch on it. Runs to building inside to Transfer Switch. Is a Additional Disconnect switch Required per Article 225.As the Generator feeders enter the building and before the Transfer switch?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
whatsup yoopersup...I say yes to your question, and it must be suitable for service equipment.
Unless the transfer equipment meets the qualifications of Article 225...
shortcircuit
Y
Found the Answer ,700.12B(6)Was added in the 2002 Code. take a look.