250.142(B) IMO is enough but you could also look to 250.24(A)(5).
Quote
250.24(A)(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.
Bob Badger Construction & Maintenance Electrician Massachusetts