#92072 02/25/05 06:07 AM
Joined: Jun 2004
Posts: 613
S
Member
When isolated (not continuous between enclosures) sections of metal conduit are used for physical protection of nonmetalic cable,like for a floor penetration for exsample, is it required to be grounded?

Code refrences please.

shortcircuit

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#92073 02/25/05 09:52 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Maybe 250.86 Exception No 2 covers the question.


George Little
#92074 02/25/05 10:38 AM
Joined: Jun 2004
Posts: 613
S
Member
Thanx George Little...and what determines the distance of "short sections"...

For example could I penetrate a plastered wall with romex, enter 30 feet of EMT with bushings on each end and exit the other end and go back into a wall on the other side of the garage without grounding the EMT at all? The EMT would be provideing physical protection of the romex.

shortcircuit

#92075 02/25/05 03:02 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
From a practical sense, the most likely places where a cable could energize the sleeve are the ends, so the length won't change that risk much. If you are talking about the raceway being energized by an unrelated circuit we fall back to the arguments about bonding that steel beam.
(and we don't want to kick that tar baby again)


Greg Fretwell
#92076 02/25/05 05:21 PM
Joined: Jun 2004
Posts: 613
S
Member
gfretwell...I was not thinking so much about the may become energized from the outside, but was thinking what would happen if this EMT providing physical protection were to become damaged itself from a inadvertent impact of some sort and then becoming energized by the circuit it protects.
Guess that I'm reaching again [Linked Image]

shortcircuit

#92077 02/25/05 05:47 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I guess the real question is how you would bond the raceway to the RX without a box to open up the jacket in.


Greg Fretwell
#92078 02/25/05 08:51 PM
Joined: Dec 2003
Posts: 751
E
Member
The same way we have to bond that steel 90 in the UG service PVC run that isn't 18 inches below grade. With a ground clamp or bushing and a wire to the ground bus in the panel.