Have a garage Apt in large house. The area is all open,except for the bathroom. There's also a kitchen,but it's all in the same area as the living/sleeping quarters.
I'm thinking the kitchen should be treated as a separate area,and wired like a normal kitchen. Living/sleeping area should be afci.
I'd ask the ahj.,but there isn't one.
Am, I seeing this right?
Russell
|
|
|
|
Joined: Jul 2004
Posts: 9,930 Likes: 34
Member
|
I'm sure it sounds like overkill but I tend to agree. The kitchen area should have 2 20s, GFCI, serving the countertop and the bath should have a GFCI 20. Everthing but the bath should be fed from AFCI breakers since it is all part of the sleeping area. I suppose it could be argued that the small appliance circuits don't need AFCI but I am not sure how you make that argument if it is all one room.
Greg Fretwell
|
|
|
|
Joined: Feb 2004
Posts: 74
Member
|
It depends on rules in your area. In my area where the sleeping facilities form part of a single room combined with other living areas, the kitchen receptacles (counter, fridge, microwave,etc) are not considered part of the "sleeping facility" receptacles requiring arc-fault protection.
|
|
|
|
Joined: Nov 2002
Posts: 558
OP
Member
|
I could see that too CRM. As for the rules in this particular case...there are none. No Permits,no inspections,and no AHJ in this particular area.
And yes it is all one room. Only partitions are around the bath.
Russell
[This message has been edited by ga.sparky56 (edited 02-13-2005).]
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
The rules for AFCI are fairly new and will be massaged in the future, as more information is gathered. As for now it is almost "experimental" in nature. What I mean by that is the requirements are for bedrooms as some "information", whether correct or not, has been presented that fires tend to start in bedrooms more than not. And they will be looking at studies to help further decisions in the future.
The studio/one room scenario might not have been considered. I do not see the harm of having it all protected by AFCIs, but that would require GFCI protection at the countertop receptacles located at the receptacles, as AFCI do not provide the proper type GFCI protection as per NEC.
For now I would permit the installation with or without AFCI protection for the kitchen area.
Remember this is strictly my opinion!!!
Pierre Belarge
|
|
|
|
Joined: Jan 2005
Posts: 354
Member
|
Cutler-Hammer does make 1-pole and 2-pole (common trip), 15-amp and 20-amp, AFCI/GFCI combination breakers for both CH and BR series panels. So in theory you could put total protection everywhere, including shared-neutral circuits. Their classified breakers for QO and HOM series do not include all these options.
This is one of the reasons I may end up using C-H in the home I'll be building in a few years (although, things can change by then).
|
|
|
|
Joined: Nov 2002
Posts: 558
OP
Member
|
Thanks for the input fellas.
To do the CYA deal,I think I'll afci everything in that apt.(except the bath) Just to err on the side of caution.
Russell