Safety at heights?
1 members (Scott35), 235 guests, and 27 robots.
#91818 02/07/05 10:54 PM
e57 Offline OP
Today I was looking around the site, and noticed the burlar alarm guy has supported the majority of his cabling on my FLS and Power/Signal conduits on this whole floor. I gave him fair warning that it needed to be removed, (Or I'd send 15 guys down there to cut into the smallest peices they could. I thought it, I didn't say it!) and that it was a code violation.
Now he has the Arch, and GC trying to get me to allow it. I will not!
But it did bring up an interesting question, and I figured I'd take it here:
What about supporting his Class 2 cable to conduits for, and containing Tel and Data or class 2 and 3?
The way I read it, the answer is no. Or is a descretion call? I'd say it's a maybe. What do you think?
725.54(d) Support of Conductors. Class 2 or Class 3 circuit conductors shall not be strapped, taped, or attached by any means to the exterior of any conduit or other raceway as a means of support.
Exception: Except as permitted by Section 300-11(b)(2).
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#91819 02/07/05 11:30 PM
300.11(B)(2) was added to allow wiring such as thermostat wires to be secured to the outside of a raceway only.
You got it right they are violating the rule you mentioned. Better to have the AHJ call this out.
#91820 02/07/05 11:31 PM
What's FLS?
Someplace in the '99 NEC it uses the words "functionally associated" as an exception. I don't know if this is the case here or not.
George Little
#91821 02/08/05 12:07 AM
e57 Offline OP
Fire-Life-Safety (Fire Alarm)
Joe, I'll bring the camera tomorrow, you'll love it!
#91822 02/08/05 08:58 PM
e57 Offline OP
Sorry Joe, forgot the camera today, and by the time I got there they had already removered most of it.