ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 248 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Joined: Oct 2000
Posts: 2,749
Member
How does the NFPA Fire Alarm Code 72 interface with the NEC?

Does the FA alarm installer have to comply with the NEC, other that Article 760?

I will appreciate some feed back please.

I see and have always approached these systems as emergency systems, and find many areas that are often overlooked.

In Massachusetts we have a C and D license classification for these installers, contractor and journeyman.

Here's a site that includes a test for the FA installer:
http://www.ieisa.com/


Joe Tedesco, NEC Consultant
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
Unfortunately the information relationship is a bit muddy between NFPA 70 and 72. Usually some building or life safety code tells you where detection is required and other aspects of the big picture, then 72 gives more application information of where and how to's, then 70 tells you about cable/wire, raceway, boxes, etc. The information in 70 is not only in 760 but in the multiple references to articles in Chapters 1-4. There is even a new smoke detector related requirement that shows up beginning in 2002, that is hiding in 645, if you frequent that part of the code.


Ron
Joined: Oct 2000
Posts: 2,749
Member
Thanks for the information Ron:

Quote
Ventilation in the underfloor area is used for the information equipment room only. The ventilation system shall be so arranged, with approved smoke detection devices, that upon the detection of fire or products of combustion in the underfloor space the circulation of air will cease.

Commentary: This requirement has been revised for the 2002 Code. The underfloor area is required to be provided with smoke detection device(s). Upon detection of smoke, the circulation of air in the underfloor area must be interrupted. The most common method of interrupting air circulation is to open the circuit that supplies power to the air circulation fan.

In addition to causing cessation of air circulation in the underfloor area, the smoke detectors may provide other fire protection functions as part of a complete building fire alarm system.


Joe Tedesco, NEC Consultant
Joined: Jan 2004
Posts: 1,507
G
Member
I find it interesting that the smoke detector only has to interrupt the air flow. It isn't required to initiate any audible or visual signals. Kinda drives home ther difference between a smoke detector and a smoke alarm.


George Little
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
If a FACP is required by the building code, then detectors installed in the building need to be connected to it and sound the notification devices. See IBC-2003 907


Ron
Joined: Jan 2004
Posts: 1,507
G
Member
Is it possible tp install smoke detectors without installing a FACP? In other words, can I use a smoke detector to control a relay and thus break a set of contacts and drop out the fan and stop the air circulation in the "Computer room"?


George Little
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
How does the NFPA Fire Alarm Code 72 interface with the NEC?
Does the FA alarm installer have to comply with the NEC, other that Article 760?

I will appreciate some feed back please.

Joe I install a fair amount of fire alarm systems and have not looked at NFPA 72 more than a couple of times.

The reason is this, I install the systems per engineered prints.

Even when we do a design build job the fire alarm prints are drawn up by an engineer. After that they go to the FD for approval.

Out at the job I get a stamped set of drawings that I can not deviate from.

The placement of devices, the number of them, how they interact with other building systems like HVAC, elevators etc. is all laid out for me.

All the issues I have input in are contained in the NEC.

Sadly that makes me just an installer and not a technician in my mind.

To be honest I do not feel qualified to design a life safety system like a fire alarm.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Oct 2000
Posts: 2,749
Member
Thanks for the feedback, I was involved in a Basic Fire Alarm Class and most of the students were electricians, some journeymen one master and a few apprentices. They too did not use NFPA 72, and when I mentioned the NEC Article 760, 300.21, 22, and 23 and other rules as they're aware, their face's all dropped.

Am I missing something, or is our trade going downhill?


Joe Tedesco, NEC Consultant
Joined: Jan 2003
Posts: 4,391
I
Moderator
I don't know if I would characterize it as going down hill, although they should be following the NEC sections you quoted.

In my mind the design of modern fire alarm systems is so complex at this point that it needs to be handled by specialists in that field.

The risk are to great and the issues can be complex.

Once you get into larger buildings with smoke evac, elevators, building automation systems, rooms in buildings with separate pre action systems, the list is endless you need someone who really knows their stuff.

The energy codes are forcing the lighting systems to shut down all the lighting when not in use so now we need a tie from the fire alarm to the lighting controls.

Elevators, you have primary and alternate floor recalls which has to be properly programed into the panel.

When we have banks of elevators the emergency generator may only be sized to run one at a time now recall must be coordinated with the specialized elevator power transfer switch.

I am happy to work of a detailed set of prints, I still have to know and follow the NEC and it still takes a craftsman to make it look good and operate correctly.


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
From a business perspective, an electrician should have a copy of NFPA 72, and be somewhat familiar with it in order to get extras! For some reason there might be 900 smoke detector on the project, and if I missed one on the Contract Drawing, that is picked up by the EC, the one extra detector always costs $2,000! I'm being funny [Linked Image], but there is lots on $$$ in change orders if you can pickup on missing stuff.
Of course I'm glad that not to many folks know 72, so that when I screw up on a design, it doesn't get thrown in my face.
That concept applies to many areas of NFPA 70 too!


Ron