Hello,

I recently bought an older house, and I have been finding problems with the wiring in the breezeway and garage that was added on in the 80’s. It appears to have been a lot of DIY work that never got inspected properly. The most recent one I have found is with the dryer receptacle. This is a 10-30R (3-wire) receptacle fed from a subpanel. I know that this is not allowed by 2002 NEC, but was the 3-wire receptacle ever allowed when fed from a subpanel? I thought it was only allowed when fed from the main panel, since neutral and ground are bonded together there. I’m just wondering if this may have been allowed by code when it was installed or if it is another example of incorrect wiring. I plan to replace it with a 14-30R, since the cable has 3 conductors plus the ground.

Brian

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2002
Posts: 163
D
Member
"but was the 3-wire receptacle ever allowed when fed from a subpanel? I thought it was only allowed when fed from the main panel"

3-wire receptacles (i.e. using the neutral to ground dryer frames) was permitted up until 1996 (?); they were permitted to originate in any panel as long as the neutral was insulated.

Quite freguently SE cable was used to wire up stoves, ovens, dryers. Some of this cable did not have an insulated grounded (neutral) conductor. You were not permitted to use this type cable inside a house unless: you were feeding stoves, ovens, dryers and the circuit originated in the service.

See 1979 - 250-60(C) & 338-3(b)

Joined: Jan 2003
Posts: 4,391
I
Moderator
I was always told 3 wire range and dryer feeds where not permitted from sub panels, I will have to check my local amendments.

[This message has been edited by iwire (edited 02-03-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Jan 2005
Posts: 9
M
Junior Member
this was common, look at 250.140 (3) in the 2002 NEC applies to existing ranges & dryers, if the grounded conductor is uninsulated it must originate at the service
equipment, and also look at 250.42 (B) exception #1 permits load side grounding, on existing ranges & dryers,

Joined: Apr 2004
Posts: 201
Member
It was permitted to feed them from a distribution panelboard but it was not permitted to use SE cable from that location. You were required to use a cable with an insulated neutral. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Joined: May 2004
Posts: 162
C
Member
My 1996 NEC in Article 250.60(c) States
The grounded conductor is insulated and part of Type SE service-entrance cable and the branch circuit originates at the service equipment.

This language was removed in the 99

Charlie

Joined: Jan 2005
Posts: 18
B
Member
Thanks for the info, everyone.

If the neutral has to be insulated from a subpanel, wouldn't there always be a separate grounding conductor in the cable, so you'd always end up running a total of 4 conductors from the subpanel? Since you'd always have the separate neutral and ground conductors, the only real reason to put a 3-wire receptacle fed from a subpanel would be to avoid changing the appliance cord, which I assume was the reason in this case.

Brian

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
Long ago I asked why you would run 10-3/wg to a 3 prong dryer outlet and the answer was that since the 3d wire is identified as a groundED conductor <some AHJs said> it had to be white, even tho it was also used as a groundING conductor. They usually attached the bare wire to the backstrap of the receptacle and the white to the ground contact. Once "the war was over" it is easy to go to the 4 pronger.