Should the generator neutral be bonded to the generator frame?
Yes, because the nuetral is switched and is therefore a seperatley derived system.
Should a grounding electrode be established at the generator?
Yes, because the nuetral is switched and is therefore a seperatley derived system.
How can I determine the available fault current of the generator for proper selection of equipment as required by 702.5
I have been told to use the KVA rating of the generator as though it were a transformer and use the infinite bus primary method. Assuming a 3% impedance you would have about 3,475 Isc available.
I=KVA/V/Z%
I=25,000/240/.03