The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Search Function
by Webmaster
01/18/17 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 09:17 PM
ESA Arc flash course
by frank
01/18/17 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 29
HotLine1 21
Ruben Rocha 16
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 184 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91680 - 01/29/05 08:33 AM Common grounding electrode,per sec#250.58
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
guys, I need help with this ons... given a large multifamliy dwelling unit has (2) services, The building has a (2)hour rated party wall halfway the building, this is not a true fire wall, therefore this is considered to be one building. my question is to comply with 250.58, to have a single grounding system, Can the bonding jumper that connects service #1 to service #2 be routed through the attic of the the building ? thanks, mj

Top
2017 / 2014 NEC & Related Books and Study Guides
#91681 - 01/29/05 08:40 AM Re: Common grounding electrode,per sec#250.58
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Mj, there is nothing prohibiting running through the attic as far as the NEC is concerned, there could possibly be a local code though.

Just be sure to use a proper "through penetration assembly" (fire cauking) when going through the rated wall.

Roger

Top
#91682 - 01/29/05 09:00 AM Re: Common grounding electrode,per sec#250.58
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
thanks Roger, I have a contractor that do not understand the purpose of 250.58 since the slap in already in, I was going to suggest routing the bonding jumper through the attic to create a single grounding electrode system.

Top
#91683 - 02/01/05 03:56 PM Re: Common grounding electrode,per sec#250.58
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
need help guys.... any more details to support sec# 250.58, commom gronding electrode where there are multiple services on one building ? I have a board meeting soon, and I need to prove my case for requiring the bonding of electrodes for all services. thanks, mj

Top
#91684 - 02/01/05 04:06 PM Re: Common grounding electrode,per sec#250.58
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
does any kwows how long this requirment has been required in the nec .... "common gronding electrode,Sec # 250.58 " I had one inspector stated that it was not required in the 1990 nec.