Safety at heights?
1 members (Scott35), 571 guests, and 40 robots.
#91593 01/24/05 09:29 PM
BigB Offline OP
On an island with a cooktop there is 6 inches of countertop on either side of the cooktop. 210-52 says at least one receptacle is required at an island measuring 12" X 24" or larger, but goes on to say that countertops separated by cooktops etc shall be considered separate countertops in applying the requirements. So this means there are two, six inch countertops. 250-52 says a receptacle is required for each countertop space which measures 12 inches and wider.
I take this to mean the island described in this case would not require a countertop receptacle(s).
Am I correct?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#91594 01/24/05 11:13 PM
Yes you are.
Speedy Petey
"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
#91595 01/25/05 10:17 PM
BigB Offline OP
Thanks Petey