Next time I see someone dragging one of those little generators back to a campsite in the woods I will be sure they drive 2 rods or show me a grounding survey
250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be grounded and shall be permitted to serve as the grounding electrode for a system supplied by the generator under the following conditions:
I'm not saying that the bonding makes a safer system, because it doesn't, I'm just saying that when you combine the definition of "premises wiring" with the rule in 250.20(B) that the winding must be bonded to a grounding electrode, in this case the generator frame.
Don