#91378 01/13/05 02:17 PM
IS IT acsecptable for the power company service line to run over liveable dwelling?If it is how far off the roof does it need to be?
#91379 01/13/05 02:23 PM
Yes, 230.24(A)
#91380 01/28/05 02:58 PM
it is acceptable so long as the point of attachment sustains a 3' clearance above roof for the roofers sake
#91381 01/28/05 03:52 PM
That 3' is only "final conductor span" leading to the service head. Normally the clearance is 8' above the roof for a distance of 3' beyond the roof edge.
#91382 01/29/05 02:02 PM
Actually, the NESC is the Code that covers the serving electric utility’s service drop clearances. The 3 ft beyond the roof’s edge is not in the NESC. [Linked Image]
Charlie Eldridge, Indianapolis, Utility Power Guy
Charlie Eldridge, Indianapolis Utility Power Guy
#91383 01/29/05 10:24 PM
What is the NESC rule for height over a roof?
#91384 01/29/05 11:19 PM
It's up to the POCO. Here they won't allow the eight foot riser if it's more than 3 feet from the edge because they don't allow the line crews to use a ladder on the roof for safety reasons. So they specify five feet, no matter how much of the drop extends over the roof.
#91385 01/30/05 10:23 PM
These are "before and after" photos of one result of a service change I did. As you can see, the service drop has a lot more clearance than it previously had.
So, yes, you can run these conductors over a dwelling, but you do need 36" clearance. While I believe that this is covered in NEC 230-24, your local utility is likely to have a different rule.
- renosteinke
#91386 01/30/05 10:39 PM
If this drop is not going to the building in question I think 230.24 says it has to be 8 feet above the roof, out to a distance of 3 feet from the roof's edge. The exception (4) is for the final span of the drop that connects to the riser on the building served
#91387 02/01/05 09:37 PM
Somehow the "before" and "after shots got reversed [Linked Image]. I hate it when that happens!
I will admit that 230 also references the pitch of the roof; this roof is right on the line, and I let the inspector decide. Part of this was based upon the heigth of the riser on the building getting new service; see photos added to "flagpoles" in "photos submitted for discussion."