#91199 01/04/05 01:46 PM
Joined: Apr 2002
Posts: 178
R
Member
While visiting another furum I read a disscusion on sub panels.They must have 4 wires back to the main panel.They also stated in the main panel the neutral and grounds must be separated and not bonded together at main panel.If you have only 3 wire service at the main panel the grounds and neutrals would have to tie or the ground fault path wouldn`t trip the breaker. Did I totally miss something.was it a type o.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#91200 01/04/05 02:01 PM
Joined: Nov 2003
Posts: 269
E
Member
I believe that either it was misstated in the discussion or you misread it but in the service equipment the EGC's and the service equipment enclosure are bonded to the grounded service conductor (i.e. the neutral). This provides the fault clearing path.


John
#91201 01/04/05 07:51 PM
Joined: Dec 2004
Posts: 86
P
Member
Do you mean:

[1] neutral
[2] (red) leg
[3] (black) leg
[4] Grounding conductor

The service does not provide a grounding conductor. That's why the service has only three conductors. The GEC at the service is where the grounding conductor comes from and it can only be connected to the service neutral at one point and that is at the service.


Sam, San Francisco Bay Area
#91202 01/04/05 07:53 PM
Joined: Dec 2004
Posts: 86
P
Member
After reading your post again. Did they leave out the main bonding jumper?


Sam, San Francisco Bay Area