#91107 12/30/04 10:04 PM
I recently installed a receptacle in a large walk-in closet at the customer's request after checking the NEC for any possible violations. I didn't find any.
Yet the Town Inspector failed it anyway citing the NEC. I called and expressed my concerns that there is no rule that prohibits a receptacle in a closet. They have not returned my calls.
As electricians may know, it is prohibited to install exposed light bulbs, overcurrent devices, and heating cables in closets.
From the NEC, a receptacle is not required. But a violation?
Have I missed something?
Or is the Electrical Inspector mistaken?
Steve Danielson
Lic Master Electrician
#91108 12/30/04 10:14 PM
There is no violation; indeed, with today's elaborate closets, receptacles are becomming common.
The NEC does prohibit installing panels in clothes closets these days---the practice was once common---and that may be what the inspector was thinking of.
In any event, it is the inspectors' duty to cite the code. Just don't jump on him if he admits to being a little confused...it happens to us all!
#91109 12/30/04 11:27 PM
I looked too and I couldn't find permission anywhere in the NEC to install a receptacle in a closet.
Of course I couldn't anything prohibiting it either.
So it's up to your inspector to come up with the goods and that should be in the form of a code reference. Ask him what code was violated. As long as you're diplomatic about it and your inspector's not phsyco you should be able to sort it out.
Sam, San Francisco Bay Area
#91110 12/31/04 10:24 AM
As an AHJ I was told by some very smart people, that "If you can't read the violation in the NEC, Then you can't write a violation!" Ask the AHJ very nicely, what code section you are in violation of so that you don't make a mistake. In NJ by law, I have to cite a violation by chapter and verse where it is in the NEC. At the very least our state has a "Construction Board of Appeals in each county. You and the inspector have the right to go in front of this board. They will hear both sides of the story and give you an answer. They will either side with you or the AHJ. Good Luck
#91111 12/31/04 10:58 AM
just put a blank cover over it until the inspector leaves and then put the recp back in.
#91112 12/31/04 02:33 PM
That's brilliant makokiller. [Linked Image] ugh
#91113 01/02/05 04:05 PM
Or hang a picture over it [Linked Image]
#91114 01/02/05 07:26 PM
This inspector may be new, if so, he can learn just like anyone else. Ignoring his citation, and not contesting it will just cause more people and maybe yourself more frustration in the future.
As has been mentioned, ask him what he is citing.
Pierre
Pierre Belarge