527
13
Hi, I figure the Subject of this message will make a few people scratch their head! If I place two ground rods 6 feet apart but hit bedrock with the second rod and it is in a 2 foot deep trench which way can i bend the rod? Towards the first or away from the first.
I got it down about 4 feet and it would not go any further.
thanks for any replies or comments..
-regards
Greg
If you're hitting solid rock, I would think you are screwed either way. I would be willing to bet that the parralleling efficiency would be better if they were angled away from each other, but I would also be willing to bet that you would not get 25 Ohms, even if you drove a half dozen of them!
Ryan Jackson, Salt Lake City
Hi, The firts rod drove in all the way, the second rod located 6 feet away went down 4' the stopped the trench was 2' deep.
Once it is backfilled isnt this in compliance?
-regards
Greg
I had a similar situation, however I could get neither rod to go more tham 3 feet anywhere on the property. I was using a Bosch demolition hammer with grd rod attachment. I finally pulled them both out (by twisting them with a pipe wrench) and drove them at a 45 degree angle. They went to the bedrock then slid along on top of it. The inspector didn't even question it.
Mustang,
I don't believe that you are permitted to bend the rod, but I believe that you are fine if you bury the _entire_ rod horizontally at a depth of 2 feet.
Where does this trench extend? Have you considered using a ground ring instead of rods?
-Jon
Winnie, Could you explain further? Why would a rod have to be straight?
mustang's right. Now I'm scratching my head
Bend the rod away from the first. The NEC only requires 8 feet of rod in contact with the earth, six feet apart. If you are concerned with the rod's length, then add a third rod in a triangular pattern.
Earl
The trench would have to be at least 2.5 ft deep. The section only talks about driving the rod to a depth of 8 ft, or where bedrock is encountered, buried in a trench. can't see where they talk about bending it, other than having 8 ft in contact with the soil.
See 250.53(G)
If you hit bedrock you are allowed to drive at up to a 45 degree angle. If you still hit bedrock at a 45 degree angle you then can bury it in a trench that is at least 30" deep.
You may not bend the rod unless its more than 8' long. You must use connectors that are rated for direct burrial.
You need to make sure that at any point the 2 ground rods are at least 6' away.
I was bored and wanted to try out my MSPaint skills