Fire pump 20hp & booster pump 3/4 hp.460volt3phase

20hp=27amps LRC=145 amps
3/4 hp=1.6 amps LRC 12.5 amps
Disconnect Size 145 +12.5=157.5
240.6 next size up 175amps
175amp disconnect switch
The way I read it from the fire pump locked rotor sized disconnect switch to fire pump controller wire sized at 125 %
27plus 1.6=28.6x125%=28.6
according to the code 175 amp disconnect switch with 30 amp wire from switch to fire pump controller then to the mtr. code handbook 2002 pages 975-976.
Please comment . Thank u

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2004
Posts: 1,507
G
Member
Yooper- I see you got it right. You must have had a good teacher [Linked Image]