We have 3 3 phase 3 HP fan motors that are
continuous duty.
Can we use cord and plug and the breaker
to operate the motors? or do we have to
use a overload section on each motor?
Thanks,
Sparky_1
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#90429 11/21/04 11:03 AM
Tom Offline
Most 3 phase motors do not have built in overload protection. You have to install an overload device in each conductor & this is usually done with a motor starter. See 430.32
As for using the cord & plug connection, that will require a horsepower rated receptacle and a horsepower rated cord cap.430.109(F)
Tom
Few things are harder to put up with than the annoyance of a good example.
#90430 11/21/04 11:51 AM
Thanks for the information Tom