#90297 11/13/04 10:15 AM
Joined: Jun 2004
Posts: 220
T
Member
Can anyone tell me where I can find dimentsions for 15kv concentric neutral cable? Customer wants it in pipe. It looks like a 500 kcmil cable, but there must be a place in the code book with the measurements for it. any help would be appreciated. Thanks, Gary

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#90298 11/13/04 10:22 AM
Joined: Jun 2004
Posts: 220
T
Member
I found it

#90299 11/13/04 11:05 AM
Joined: Apr 2004
Posts: 201
Member
It is not recommended to put concentric neutral cable in conduit, it is intended to be direct buried. If you wish to put it in conduit, get jacketed concentric neutral cable. Over the years, we have bad performance from concentric neutral cable in conduit. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
#90300 11/14/04 11:18 AM
Joined: Jun 2004
Posts: 220
T
Member
charlie, what performance problems ? We are going to put it in PVC. What do you mean by jacketed, I tought it already had a jacket on it(Black jacket with pinkish insulation inside)? It is listed for direct burial, but the customer wanted it in pipe. If we bury it without pipe, still would need a riser. Would this hurt the wire also? Always good to get advice from the other side of the fence.Thanks, Gary

#90301 11/14/04 11:12 PM
Joined: Apr 2004
Posts: 201
Member
We have put miles of cross-linked solid dielectric bare concentric neutral in the earth with some in PVC conduit. We have had a lot of failures with the cable in the conduit. We quit using the bare concentric neutral and went to a polyethylene jacket over the concentric neutral cable and have had no trouble with the jacketed concentric neutral cable. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
#90302 11/18/04 09:48 PM
Joined: Aug 2001
Posts: 599
N
Member
Charlie,
Did you ever pin point why the cable was failing? The utilities here run it in PVC all the time.

#90303 11/18/04 11:11 PM
Joined: Apr 2004
Posts: 201
Member
I seem to remember a problem with arcing between the concentric neutral conductors and the outside of the cable.


Charlie Eldridge, Indianapolis Utility Power Guy