#90222 11/03/04 02:01 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Are plastic boxes ok to use in commercial buildings? Some do have a knockout for pipe or mc cable to run into.


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2003
Posts: 269
E
Member
Non-metallic boxes cannot be used with metallic wiring methods unless meeting one of the two exceptions. 314.3.


John
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Why then is there a 1/2" knockout? for PVC? What would be wrong with plastic boxes, there used in homes?


The Golden Rule - "The man with the gold makes the rule"
Joined: Apr 2002
Posts: 558
C
Member
The non-metalic boxes with standard K.O’s are for ENT (smurf tube) or can be used with RNMC. There is nothing wrong with non-metallic boxes when used with non-metallic wiring methods. You can’t use metal raceways or cable armors with non-metallic boxes since the raceway or armor would not be properly bonded.

Curt


Curt Swartz
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
caselec,
Yes true, unless you run metal cable from a bonded metel panel to the plastic box, then its bonded at one end.


The Golden Rule - "The man with the gold makes the rule"
Joined: Feb 2003
Posts: 198
Z
Member
electricman2 has the correct response.
I wonder if a twin M/C connector would satisfy the exception to 314.3?