ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 422 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#89971 10/26/04 09:48 AM
Joined: Sep 2004
Posts: 86
N
Member
Have a 100 amp main breaker panel in a residence. Have to add a sub panel and plan to feed it with #4's and use a sub feed lug instead of a breaker. The sub panel is then protected by the 100 amp main breaker. Any code violation here?
Ron

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#89972 10/26/04 10:30 AM
Joined: Sep 2003
Posts: 650
W
Member
I would double check the stab ratings on the main panel that is feeding the sub. Some panels limit the maximum current ratings of loads connected to a single bus stab.

Also the use of #4s falls right onto an ugly bit of NEC 310.15(B)(6). #4Cu is permitted to be protected with a 100A OCPD when it is used to supply the _main_ power feed of a single residence. #4Cu does not have sufficient ampacity to be protected at 100A _in general_, but for the specific load described in 310.15(B)(6) it is permitted to do so. This means that #4Cu is _not_ sufficient for the feed to a 100A subpanel.

But there is yet another exception, which is that the feed to any subpanel in a residence is not required to be larger than the main feed. So I think that using the #4Cu as you describe will be okay until such time as the main service is upgraded, at which point you will need to protect the subpanel at less than 100A.