#89722 - 10/16/04 03:45 PM working clearance 110.26
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
NEC 110.26 requires working clearance in front of equipment likely to require calibration, testing, or adjustment while energized. This means a 30 by 36 inch space (or larger) in front of panels, access panels on HVAC equipment and fused disconnects.
Does this requirement extend to non-fused disconnects? I am thinking specifically of the service disconnects often found installed 12-18 inches behind AC compressors in the side or back yard of dwelling units.
_________________________
Earl
Top
2017 / 2014 NEC & Related Books and Study Guides
#89723 - 10/16/04 04:11 PM Re: working clearance 110.26
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Earl, I personally don't think it would apply to a switch, but take note and get ready, this oppinion will be debated shortly.

Roger
Top
#89724 - 10/16/04 04:21 PM Re: working clearance 110.26
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I am with Roger on this.

Further considering OSHA all but forbids working on things hot, what is the point anyway.

I am on a job now that the inspector is requiring the plumber to install the electric hot water heater to 110.26 on the side with the elements.

Does anyone normally change water heater elements live?

[This message has been edited by iwire (edited 10-16-2004).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89725 - 10/16/04 04:33 PM Re: working clearance 110.26
capt al Offline
Member
Registered: 06/20/04
Posts: 206
Loc: Norton, Ma USA
Roger, Why would you think your opinion would be debated? I'd agree with you. What would be serviced "while energized" in a non fusible disconnect switch?

Al
Top
#89726 - 10/16/04 04:52 PM Re: working clearance 110.26
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
When there is a problem with a piece of equipment the first thing many troubleshooters will do is check for voltage at the load side of the disconnect serving the equipment. This requires 110.26 work space. Even OSHA permits troubleshooting hot.
Don
_________________________
Don(resqcapt19)
Top
#89727 - 10/17/04 01:02 AM Re: working clearance 110.26
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
I'm with Don on this one.

On another note, a while back I had an inspector call for workspace in front of phone equipment terminals. Hey, I'm all for it keep crap out of my way.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#89728 - 10/17/04 07:48 AM Re: working clearance 110.26
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
As the installing electrician, I would like to keep the area in front of my disconnecting switch relatively clear. As the inspector, I can, and do, cite the electrician for not leaving working space in front of the disconnect. As the trouble call electrician I have wished the installing electrician had left enough room in front of the disconnect for me to be able to test for voltages without having to perform contortions.
I have heard of this call being made by other inspectors where it was OK to crowd the disconnect behind equipment if there was another disconnect before the "workman's switch" that could be locked in the off position. The explanation given was the workman's switch wasn't even required, so it needn't have a working clearance.
As an electrician, I have also had to install disconnects behind equipment, knowing there wasn't enough "working clearance" room because there simply wasn't room to install it anywhere else.
How do you guys handle that situation?
Does it make a difference if the switch is a ball-bat type with a screwed-on faceplate or if the switch is a HD safety switch with a hinged cover easily opened for voltage testing?
This is how I have differentiated between the two situations in the past: Is it likely to be used for voltage testing? If yes, then you need a working clearance. Who agrees? Who doesn't?
_________________________
Earl
Top
#89729 - 10/17/04 08:38 AM Re: working clearance 110.26
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
How do we handle switches above counter tops?

These don't have 110.26 clearances and a switch is a switch, we can't use the argument "that those don't count".

Roger
Top
#89730 - 10/17/04 09:47 AM Re: working clearance 110.26
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
This working space issue is always going to be a judgement call. Who is to say that the disconnect behind an AC is more likely to need service than the receptacle under the sink for the disposal. As soon as you make a decision, you will be wrong on your next service call. Anyone who has crawled on his belly in a 140 degreee 3:12 attic full of blown in insulation, looking for a J box, will question the "accessible" rule too. :-)
_________________________
Greg Fretwell
Top
#89731 - 10/17/04 10:04 AM Re: working clearance 110.26
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I'm with Don as well. I don't think fuses enter into it.

I also see everyone elses point as well, which is why I have been working on a proposal (for months now) to change the text of 110.26 to include a list format of the equipment it applies to, but that brings up its own issues as well. It really is a difficult subject.
_________________________
Ryan Jackson,
Salt Lake City
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals