#89266 09/13/04 07:00 PM
Joined: Dec 2003
Posts: 886
H
Member
I asked a honeywell tech what the ground was used for and was told it was only to protect the P.C. board from damage caused by arcs as well as surges coming off of the monitoring phone lines.

Don't know about the arcs but he brings up a point I touched on in my first post. If the panel is connected to a telephone line there are surge protectors from each side to ground to protect the circuitry. Many panels have surge protection on the terminals connecting to the premises wiring also particulary if there is a possibility that they may be run outside.

Another reason for a proper ground.

-Hal


[This message has been edited by hbiss (edited 09-13-2004).]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#89267 09/13/04 08:37 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
"What a great code question!"
True, very true!
I still say to the EGC of the circuit, as it is a guaranteed ground/bond to water, service, and phone. Be it code or not.(my opinion)
Not to mention a lot easier than the alternatives... Except not doing it at all.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#89268 09/13/04 09:35 PM
Joined: Jun 2004
Posts: 613
S
Member
Well...tuff question I guess.Does the 2002 NEC allow a cold water pipe(beyond 5ft from the point of entrance to the building) for connection of a grounding conductor?
The definition of equipment grounding conductor is "The conductor used to connect non-current-carrying metal parts of equipment,raceways, and other enclosures to the system grounded conductor ,the grounding electrode conductor, or both, at the service equipment or at the source of a seperately derived system"
The wording "at the service equipment" or "at the source of a seperately derived system" implies that equipment grounding conductors must be run to the service equipment.
250.130 instructs on how the connection shall be made.
My answer is NO the 2002 Nec doesn't allow the connection to a metal water pipe beyond 5ft of the point of entrance of that pipe to the building.
The instruction with the alarm panel must be outdated.

shortcircuit