Electricians revenge
0 members (), 192 guests, and 14 robots.
#89080 08/30/04 03:42 PM
680.23(A)(5)says that pool lights shall be installed so that the top of the lens is not less than 18 inches below the normal water level.
Well the pool company installed some low voltage lights at just 8 to 10 inches below the water level...12 volt 300 watt wet niche type (Hayward) and the inspector does not want to accept the installation.
Is it so very important to have these lights down 18 inches?Would any of you inspectors accept low voltage lights at this depth??
#89081 08/30/04 04:14 PM
I am not an inspector but I would not ask one to change requirements in this section.
In the NEC Handbook they give an explanation of this rule, it is an opinion not an official interpretation. [Linked Image]
Handbook Commentary after 680.23(A)(5)
The reason for the 18-in. minimum submergence requirement is to reduce the likelihood that a person in the water and hanging onto the side of the pool directly over the fixture will have his or her chest in line with the fixture. This section covers fixtures that have been investigated and found acceptable for use where a person's chest may be directly in front of the fixture. The highest level of leakage current in the pool coming from a wet-niche fixture with a broken lens and bulb is found directly in front of the fixture.
Sounds like a good reason to follow the code. [Linked Image]
#89082 08/30/04 04:37 PM
It says "unless the luminaire is listed and identified for use at lesser depths"
Do you have any specific information on the Fixture?
#89083 08/30/04 05:23 PM
Bill...I've asked for installation instructions for the pool light from the pool company,who supplied and positioned the lights at that depth when they set up the forms for the concrete pour.It is going to be VERY difficult to change the lights at this stage.
shortcircuit
#89084 08/30/04 10:17 PM
Sounds like some one made a very expensive mistake. Unless the fixture is listed for less than 18" depth and you can prove it to the inspector. Who ever installed the fixture niche is out some serious money
ed
#89085 08/30/04 10:22 PM
At this point it might be cheaper to go with a fiber light but they are pricy!
#89086 08/31/04 12:16 AM
e57 Offline
Not trying to make light of it... but make the pool deeper!