#89034 08/27/04 11:02 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I think you will find most breakers over 30a are rated at 75c. There is no point most of the time with 30 or less because of 240.4(D)


Greg Fretwell
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#89035 08/28/04 10:08 AM
Joined: Jun 2004
Posts: 220
T
Member
I agree that most breakers 30A and over are rated 75 degrees, but the original post said he could not find the markings saying that. Which refers you to 110-14(c)1 for circuits rated(based on breaker size) 100 amps or less to use 60 degree column in T310-16. Now in all likelyhood, the terminals are 75 degree, but I say if the terminals aren't identified for 75 degree, then that section must come into play. strictly speaking. [Linked Image]

#89036 08/30/04 05:02 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Trekkie I am still not following you, the post states a minimum circuit ampacity of 110 Amps. 110 amp equipment has without a doubt 75 C terminals.

Lets say I have a 90 amp breaker that the terminals are marked 1/0 but not marked as to temperature.

Would you agree that this breaker has 75 C terminals?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#89037 08/30/04 08:05 PM
Joined: Jun 2004
Posts: 220
T
Member
I agree that a breaker marked with the wire size (#1AWG or larger) by association, is listed for 75 degree. The problem is the orginal post stated no markings. I am just saying that, without any markings at all, the terminals are based on 110-14(c)1+2. which is based on breaker size or wire size, but the terminals are unmarked, so we go with circuit(breaker) size as the manufacter sets. I am not sure why they are fusing a 110 MCA at 100 amps(max breaker), but they are the manufacuter, and they must have had to send it to UL or something to market the product. I don't doubt that they aer 75 degree terminals, but strictly speaking without evidence of what the terminal is suited for, 110-14 comes into play.