ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (CoolWill), 250 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Feb 2004
Posts: 41
R
rknikko Offline OP
Member
In NEC 2002 Code, how far apart do we need a receptacle outlet in the kitchen countertop? Is it every 4ft from outlet to outlet? What about spaces separated by range tops, refrigerators, or sinks? Please help. Thanks.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
C) Countertops. In kitchens and dining rooms of dwelling units, receptacle outlets for counter spaces shall be installed in accordance with 210.52(C)(1) through (5).
(1) Wall Counter Spaces. A receptacle outlet shall be installed at each wall counter space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space.
(2) Island Counter Spaces. At least one receptacle outlet shall be installed at each island counter space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater.
(3) Peninsular Counter Spaces. At least one receptacle outlet shall be installed at each peninsular counter space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. A peninsular countertop is measured from the connecting edge.
(4) Separate Spaces. Countertop spaces separated by range tops, refrigerators, or sinks shall be considered as separate countertop spaces in applying the requirements of 210.52(C)(1), (2), and (3).
(5) Receptacle Outlet Location. Receptacle outlets shall be located above, but not more than 500 mm (20 in.) above, the countertop. Receptacle outlets rendered not readily accessible by appliances fastened in place, appliance garages, or appliances occupying dedicated space shall not be considered as these required outlets.
Exception: To comply with the conditions specified in (a) or (b), receptacle outlets shall be permitted to be mounted not more than 300 mm (12 in.) below the countertop. Receptacles mounted below a countertop in accordance with this exception shall not be located where the countertop extends more than 150 mm (6 in.) beyond its support base.
Dwelling unit receptacles that serve countertop spaces in kitchens, dining areas, and similar rooms, as illustrated in Exhibit 210.26, are required to be installed as follows:
(1) In each wall space wider than 12 in. and spaced so that no point along the wall line is more than 24 in. from a receptacle
(2) Not more than 20 in. above the countertop [According to 406.4(E), receptacles cannot be installed in a face-up position. Receptacles installed in a face-up position in a countertop could collect crumbs, liquids, and other debris, resulting in a potential fire or shock hazard.]
(3) At each countertop island and peninsular countertop with a short dimension of at least 12 in. and a long dimension of at least 24 in. (The measurement of a peninsular-type countertop is from the edge connecting to the nonpeninsular counter.)
(4) Accessible for use and not blocked by appliances occupying dedicated space or fastened in place
(5) Fed from two or more of the required 20-ampere small-appliance branch circuits and GFCI protected according to 210.8(A)(6)
For the 2002 Code, the maximum permitted height of a receptacle serving a countertop was revised in 210.52(C)(5) upward from 18 in. to 20 in. as a practical consideration.


Greg Fretwell
Joined: Mar 2003
Posts: 3
Z
Junior Member
Would it be acceptable to use plugmold under the upper cabinets with outlets on 6 inch centers if the plugmold strips were connected to the feed through wires on a pair of GFCIs? Assuming the cabinets were less that 20 inches above the counter. This puts the receptacles out of sight, clears the backsplash and provides more overall outlets on closer spacing.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I can't think of a reason why plug mold facing down would be a problem. They just frown on receptacles facing up.


Greg Fretwell