1 members (Scott35),
152
guests, and
14
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jul 2004
Posts: 787
OP
Member
|
I am assisting in moving a machine shop into a new to us building. The building service is 1200A 240V Delta with a center-tapped phase.
All subpanels located on perimeter walls have only 4 conductors run to them. The 3 phases and the neutral. I am concerned about a lack of grounded Earth conductor. All of the subpanel feeders appear to be run thru EMT buried in or below the concrete slab floor. The building is corrugated metal on a steel I beam frame. The bases of the I Beams are sitting on the foundation walls. I do not see any bonding jumpers from the steel to earth, and only at the building's main CB do I find some sort of bonding jumper.
ASSUMING the neutral is bonded to the building steel, is it OK to install the listed ground bars for the subpanels and bond them to the EMT coming out of the concrete and also to the building steel?
I have been told that the job will not be inspected. Never the less, I am pushing to do the job right.
Thanks
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
The EMT is being used as the required equipment grounding conductor for the feeders to the sub-panels. Installing an equipment ground bus to the cabinet should suffice. You could install a grounding bushing or a ground clamp to the EMT & connect it to the equipment ground bus if you want.
I don't believe that connecting each sub-panels equipment ground bus to the building steel will have much benefit.
Tom
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
Our AHJ would have a fit: EMT in the slab! Be it setscrew or compression, I have yet to see an EMT coupling I would trust to carry fault current having been exposed to wet soil. The high threshholds of OCPDs in motor circuits, the nature of the usage -- craftsmen stomping around with metal in their hands, in a metal building with metal encased motors sitting on a semi-dielectric pad.... I would want separate bonding conductors. My AHJ would insist on abandoning the old work entirely. End of story. ( I had the 'good fortune' to step in as foreman on just such a 'red tag'. )
Tesla
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Tesla: What code section wouls your AHJ cite? 358.10 Uses Permitted. (A) Exposed and Concealed. The use of EMT shall be permitted for both exposed and concealed work. (B) Corrosion Protection. Ferrous or nonferrous EMT, elbows, couplings, and fittings shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject to severe corrosive influences where protected by corrosion protection and judged suitable for the condition.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
Whose judgement about the suitability of EMT is used? The AHJ? If the AHJ judges the EMT fault path inadequate, then it shifts the burden of proof to the owner (electician, engineer?). Right?
Earl
|
|
|
|
Joined: Apr 2002
Posts: 197
Member
|
Emt is not allowed underground in Wisconsin. Does NH have a state code?
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I would say underground is different from being in the slab and as Ryan has pointed out it is one of the uses allowed.
Larry are you sure it is EMT?
I often use EMT down to the slab and then change over to RMC.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jul 2004
Posts: 787
OP
Member
|
"Larry are you sure it is EMT?" The conduit coming out of the concrete appears to be the same diameter as the EMT coming out of the panels, and they did use the setscrew style couplers.
The worksite is actually in Vermont, right across the river.
The subpanels in question are 150A and 200A panels.
|
|
|
|
Joined: Jul 2004
Posts: 787
OP
Member
|
Well its been almost a year, and we finally moved the rest of the company into this building.
I still have concerns about the ability of the grounding paths to handle any significant fault currents.
My thought is to test the resistance of the ground paths by using a welder to supply a controlled current of 100-200 Amps for a few seconds between the subpanel ground bar and the building's service bonding location and then measuring the voltage drop between the subpanel ground bar and the building's central ground.
Obviously this would have to happen with the subpanel deenergized, along with suitable Kelvin connections to ensure we are only measuring the voltage drop along the ground path and not the v drop across the welder to ground bar connection. Also we would need enough people to look for unexpected arcs or excessive heating across any high resistance ground paths.
Assuming I can get permission to perform these tests, what would be an acceptable range of voltage drops?
Larry
|
|
|
Posts: 264
Joined: February 2013
|
|
|
|