iwire Well thanks for the response everyone, I have a follow up question.
I go to a house that has a 100 amp service that is in excellent shape, the load is OK but I do not have enough spaces for all the circuits. Example 1) Why can't I just change the panel to a 200 amp 42 circuit panel leaving the 100 amp service conductors?
If you used an MLO panel with a back fed 100 ampere breaker, disconnect tie down, and a valid load calculation then it would be code compliant.
Example 2) By using 230.90(A)(1)Exception No. 3 I could leave the existing 100 amp panel and add one right beside it.
Once again if the load calculation is valid then where's the hazard?
I do not understand the logic here?
How is example 2 any safer than example 1
I'm not unsympathetic to your concern. Perhaps the submission of language to require each disconnect to have no larger ampacity than the load it serves would require would partially address your concern.
--
Tom Horne
[This message has been edited by tdhorne (edited 06-07-2004).]