Here's the problem: I have a 400 ampere feeder (Fused at 400 amperew) and I'm taping to feed a 40 ampere load using a 60 ampere saftey switch and installing 40 ampere fuses to protect my 40 ampere load conductors. What size wire should I use from the feeder tap to the 60 ampere disconnect? (Using THHN in a damp location).
George Little
#88337 05/28/04 09:36 PM
Forgot to tell you the tap is 8 feet long.
George Little
#88338 05/28/04 09:46 PM
I would say #8
Ryan Jackson,
Salt Lake City
#88339 05/28/04 10:02 PM
George you ask some interesting questions. [Linked Image]
Assuming a lot here, but if all the requirements of 240.21(B)(1) are met I agree with Ryan 8 AWG copper.
Now one for you, or anyone, what size grounding conductor is needed from the point of the tap to the 60 amp disconnect?
Bob
#88340 05/29/04 12:20 AM
but shall not be required to be larger than the circuit conductors supplying the equipment.
#88341 05/29/04 05:55 AM
Yes, but the question remains. [Linked Image]
#88342 05/29/04 08:38 AM
The tap conductors are the conductors feeding the equipment and so the EGC is #8. Table 250.122 requires a #3 EGC for a 400 amp OCPD, but #3 is larger than the conductors feeding the equipment and the EGC is not required to be larger than the conductors feeding the equipment.
Don
#88343 05/29/04 09:31 AM
IMO a lot of people would size the conductor I am asking about based on the 40 amp fuse which would be 10 AWG copper which will be correct on the load side of that 60 amp disconnect.
I wanted to point out that the EGC on the supply side of the 60 amp disconnect will need to be based on the 400 OCP.
That would normally be a 3 AWG but for this application, will only need to be 8 AWG as the supply conductors are only 8 AWG.
I thought Georges example was perfect for pointing all this out, [Linked Image] only a little off topic.
Bob
#88344 05/29/04 09:37 AM
FWIW I would wire this disconnect up with 6 AWG, the length is short the difference in price and difficulty will not be a big deal.
Besides all I do is order the stuff, I do not pay for it. [Linked Image]
JMO, not required, Bob
#88345 05/29/04 03:51 PM
dfe Offline
I agree with Iwire
#6 for the full load amps of the 60/as ( in the future you could change the load without rewire the whole mess )
#10 ground
all wire thwn ( damp location )
As long as the total wire lenth of the tap is less then 10'