#88346 05/29/04 04:39 PM
Joined: Apr 2002
Posts: 558
C
Member
dfe

How do you come up with a #10 EGC?

Curt


Curt Swartz
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#88347 05/29/04 08:22 PM
Joined: May 2004
Posts: 19
D
dfe Offline
Member
How did I come up with a #10 EGC?

Jump ahead of myself and made a mistake. Good thing there are sharp people around that catch mistakes like that. I would like to change that to a #2 ( #3 is ok but lots of short lengths of #2 in the shop)

Thanks Curt
P.S. Keep a eye on me I do that now and then.

#88348 05/29/04 08:47 PM
Joined: Apr 2002
Posts: 558
C
Member
dfe

Bob posted this question to test everyone here and expected to get some wrong answers.

The equipment ground should be sized from Table 250.122 using the rating of the overcurrent protection which in this case is 400 amps and would require a #3 cu conductor. As Don and Bob pointed out your equipment ground doesn’t need to be larger than your ungrounded conductors so in this case a #8 cu conductor could be used. If you decided to use #6 cu conductors for the tap then you would need to use a #6 EGC.

I hope you and everyone else here are having a great weekend!

Curt

P.S Can we call you by a name other than dfe? [Linked Image]


Curt Swartz
#88349 05/29/04 11:01 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Thank you Curt. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#88350 05/30/04 12:00 AM
Joined: Feb 2003
Posts: 939
F
Member
bob [ Iwire ]


tell me if i get this question right about the tap rules here the max length for the tap is 25 feet aka 8 meter length rules too.

but what happend if the tap do run at 33 feet [ 10 meter ] length then the rules do change too ??

i just want to clear up this question before it get out of the hand here because i did see few tap do run more than 25 feet [7.5 meter] but i was not sure if that is the case the conductors have to be same as ocpd amprage rating or larger like main cables ??

please let me know because i dont have 02 code book with me right now all i have is 96 codebook with me it say on there on art 210-19 and 364-12 but if that did change please do correct me on this one.

merci , marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

#88351 05/30/04 08:24 AM
Joined: Jan 2004
Posts: 1,507
G
Member
As to my orginal post, IMHO my answer agrees with Bob (IWIRE). If we assume 75 degree terminations, which is what we see most of the time, the wire feeding the device, which is the 60 ampere disconnect switch, would have to be #6 valued at 65 amperes. If we look at 240.21(B)(1)b., it says the tap conductor can not be "less than the rating of the device supplied by the tap conductors". Since we are feeding a 60 ampere device (see Definitions), the conductors must be at least 60 ampere capacity. If we were feeding a MLO panel that did not require a main, for example a 100 ampere MLO, the tap conductors would have to be rated at 100 amperes. If we were feeding a 40 ampere inline fuse or a circuit breaker the tap conductors could be rated 40 amperes. As for the equipment ground wire Don has made it clear and I agree that the EGC does not have to be larger than the ungrounded conductor. 250.122(A). These conductor sizes are based on the 10 foot tap rule covered under II Location 240.21


George Little
#88352 05/30/04 08:34 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
The 40 amp fuse is a device also. [Linked Image]

240.21(B)(1)(1)(b)
Quote
Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent-protective device at the termination of the tap conductors.


IMO even with 60 C terminations 8 AWG is code compliant.

My own choice would be at 6 AWG for this.

[This message has been edited by iwire (edited 05-30-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#88353 05/30/04 10:02 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Yes the 40 ampere fuse is a device but you are not feeding it directly. You are feeding the 60 ampere switch which has the potential of having a 60 ampere fuses (device) installed in it. If we wee feeding a circuit breaker and terminating our tap on the circuit breaker, we would size oru tap to the circuit breaker. As to the ampere rating of the device terminations, 110.14 would have us using the 60 degree column for equipment 100 ampere or less unless identified for higher temperature rating. If we are using 90° rated conductors the ampacity must be selected from the 60° column when 60° terminations are used.


George Little
#88354 05/30/04 10:25 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
George as I said I like the idea of sizing the wire to the disconnect but don't you think the use of the word "or" in 240.21(B)(1)(1)(b) allows us to size to the fuse?

This all seems pointless when we talk about 40 amp fuses in a 60 amp disconnect. 6 or 8 AWG is almost no cost difference, but change the load to 410 amps, you would need a 600 amp disconnect switch, the cost of providing 600 amps to the switch instead of 410 amps will be significant.

Is it your interpretation that the tap conductors to a 600 amp fused disconnect would need to be say 2 sets of 350s (620 Amps) instead of one set of 600s (420 Amps)?

I do not agree, IMO the use of "or" in 240.21(B)(1)(1)(b) allows us to size to fuse or breaker ratings.

If the NFPA meant it only to apply to breakers I feel they would have used the word 'breaker' in place of 'overcurrent protective device' in 240.21(B)(1)(1)(b).

JMO and I am interested in other peoples opinions too.

Bob

[This message has been edited by iwire (edited 05-30-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#88355 05/30/04 11:20 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Marc

Quote
tell me if i get this question right about the tap rules here the max length for the tap is 25 feet aka 8 meter length rules too.

but what happend if the tap do run at 33 feet [ 10 meter ] length then the rules do change too ??

I think you are swapping standard for metric measurements.

The lengths of taps that I know of are taps not over 3 m (10 ft) Long and taps not over 7.5 m (25 ft) Long.

Quote
i did see few tap do run more than 25 feet [7.5 meter]

If you did see a tap over 25' IMO it is not a tap, it is be a feeder and has to be protected at the supply end not at the load end of the conductors.

There are times outside for transformer secondary conductors you can tap longer than 25' feet. Service conductors come to mind.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts