Is there a minimum and maximum height for a wall mounted panelboard (service entrance and sub panels)?
Thanks
Steve
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#88290 05/27/04 12:49 PM
6'7" to the heighest breaker, no minimum height specified except for mobile homes.
Ryan Jackson,
Salt Lake City
#88291 05/27/04 01:24 PM
Ryan_J
Is there a reference I could go to?
Is the 6'7" height the height of the actual top CB or the top of the box?
Thanks
Steve
Thanks
Steve
#88292 05/27/04 01:33 PM
404.8 Accessibility and Grouping.
(A) Location. All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.
don
Don(resqcapt19)
#88293 05/27/04 01:34 PM
404.8(A)
6'-7" to the center of the operating handle in the highest position.