ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by HotLine1 - 04/23/24 02:17 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 231 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#88150 05/12/04 12:15 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Quote
No permit and no inspection required where this is located
cmv,

That does not mean that it's not a good idea if you are really interested in Safety.

Bill


Bill
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#88151 05/13/04 02:48 AM
Joined: Jun 2001
Posts: 642
N
Member
This now sounds like a farm/ ranch installation. Have your quoting electricians show you Article 547 in the 2002 Code or the adopted code in your area.
Personally I would recomend you have 4 wires into each building served by the on pole disconnect. The on pole disconnect is your service or should be made the service. All other panels are sub panels. This will entail more work, but IMHO be the best way.
good luck.


ed
#88152 05/13/04 02:52 PM
Joined: Mar 2001
Posts: 345
T
Member
Is this a farm or ranch? Are any livestock kept there?

If there are no other conductive pathways such as telephone wires, water piping, gas piping, and so forth that connect the separate building together than you can rewire it just as it is.

If there is any other metallic pathway between the buildings then you must run separate ground and neutral conductors.

In either case you must install a grounding electrode system at each building and use it to ground the building disconnecting means enclosure.

Your new panel would need it's main breaker in either case to serve as the building disconnecting means.
--
Tom Horne

[This message has been edited by tdhorne (edited 05-18-2004).]


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
#88153 05/16/04 05:34 AM
Joined: Jun 2003
Posts: 681
P
Member
With your own confusion and inadequate description of the work, it is impossible to give you a proper answer. Your best bet is to get an official inspector there whether or not it is required and have him evaluate the situation.

Pierre


Pierre Belarge
#88154 05/19/04 12:16 PM
Joined: May 2004
Posts: 4
M
Junior Member
imho i would pull the disconect at the pole replace it with two separet disconects one for each building install a new feed line to house.