1 members (Scott35), 505 guests, and 14 robots.
#88063 05/07/04 09:07 PM
I would like to back up a second. Why do you have to run a #6 wire? It's a 50 amp circuit, why not run #8 THHN?
#88064 05/07/04 10:20 PM
Mick
Take a look at 110.14(C)(1)(a) and then go to 310.16. The unit may not be listed and identified for 75C wire.
#88065 05/08/04 01:02 AM
aldav53 Offline OP
# 8 is good for 48 amps, and it is a fairly long run anyway.
#88066 05/09/04 06:34 AM
Z
Most of the Hot Tubs I have wired required # 6 cu conductors,as per manufacturer instructions.
How hot are the attics in your area? You will need to adjust your amps. Also you cannot sleeve NM outdoors, it is still a wet location,even above grade.
#88067 05/09/04 10:47 PM
334.80: NM must be used at the 60* ampacity which is 40A for #8 and 55A for #6. If you run thhn in conduit then the ampacity will be 50A and 65A respectively if the terminations are marked 75*. I'm assuming that no other derating will be necessary.
#88068 05/09/04 11:02 PM
If you are running it in the attic (typical here in NY for the summer is about 120 degrees F), that would take a multiplier of .75 times 65 amp (for 6 AWG) which is now rated for 48.75 amps.
Pierre
Pierre Belarge
#88069 05/10/04 01:21 AM
aldav53 Offline OP
The attics here in AZ do get hot, probably more than 120 deg. The spa calls for a 50 amp circuit. Derating the #6 might put it close. It would not make sense to do a splice just to run THHN through the pipe in that short run too the disc from the attic.
#88070 05/10/04 02:05 AM
I agree splices could create possible unwanted problems in the future.Best to not
splice the wire if possible.
