1 members (Scott35), 220 guests, and 11 robots.
#87616 03/26/04 08:02 PM
citysis Offline OP
I need clarification on code in NYC for gfci's.
In a residential kitchen, is the outlet within 3' of the sink 'required' to be gfci or 'recommended' to be gfci?
#87617 03/26/04 08:47 PM
I don't know the NY code, but in the NEC all outlets that serve the kitchen countertops must be GFCI protected.
Don
#87618 03/26/04 09:16 PM
Ron Offline
The NYC Electrical code has not modified the NEC-1999 Article 210-8.
All recepts that are installed to serve counter top surface require GFCI. There is no distance requirement.
Ron
#87619 03/27/04 09:12 AM
citysis Offline OP
I thought as much but wasn't sure that it wasn't ammended. thank you all very much for the info.
#87620 03/27/04 09:49 AM
When was the outlet in question installed?
This is an important part of the formula that hasn't been stated. Left to the NEC, the only regulation that applies to a kitchen counter receptacle is that which is in effect at the time of installation.
Is the outlet in question existing, proposed, or newly installed?
Al Hildenbrand