Hi, Is there a requirement for In Use Covers for outlets on a temp-pole?
thanks for any replies.
Mustang
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Yes, see 527.2 All Wiring Installations. (A) Other Articles. Except as specifically modified in this article, all other requirements of this Code for permanent wiring shall apply to temporary wiring installations.
Look for the rule in Article 406
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
Hi, Thanks for the reference. I will look it up.
I appreciate the reply.
Sincerely,
Mustang
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Mustang spend the money on some really large metal in use covers for use on temps.
The plastic ones get broken in no time leaving you with a possible OHSA fine.
Also the cords used on construction sites are not typical home owner size cords, you will need the large in use covers to close over the heavy cords.
Red Dot makes some nice ones and I am sure others do to.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
Hi, Thanks for the reply. I never have cared for the plastic see through covers. They may be more expensive than the Red Dot. I paid around $9 for a Horizontal GFCI Cover that was pot metal. I am like you though, the metal ones are more durableEspecially on a temp pole that is goingto be moved from time to time.