#87371 02/23/04 09:34 PM
Joined: Nov 2002
Posts: 267
W
Member
In parallel wiring, when sizing the ground,do you parallel the ground and figure each ground at full rating. In other words, if you have parallel 350s to give you 600 amps, do you pull each ground rated at 600 amps, or do you figure each at 300 amps. I would think you would figure each at 600 amps for full protection. This is for grounding raceway and equipment.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#87372 02/23/04 10:20 PM
Joined: Feb 2004
Posts: 2
J
Junior Member
NEC 250.122(F)(1) Size them based on the upstream overcurrent device as shown in Table 250.122. i.e 600A = minimum #1 Copper

Jim

#87373 02/24/04 01:23 PM
Joined: Nov 2002
Posts: 267
W
Member
Thanks Jim;
That was exactly what I needed.

~Andy