#87343 02/16/04 03:35 PM
Joined: Mar 2003
Posts: 849
Y
Member
Where do I find a Chart giving full load amps for 4160 volt mtrs. from say 100hp to 1000 hp???

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#87344 02/16/04 06:30 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
For 4000V motors [usual nameplate for motors used in 4160V systems] you could use 58% of the 2300V column currents in NEC Table 430-150 3ø Motor Full-Load Current (60-500hp.) Or, using the kVA/hp equivalent, a 100hp 4kV motor would be about 14½ amps and a 1,000hp motor would be ~144 amps.

#87345 02/17/04 03:42 PM
Joined: Mar 2003
Posts: 849
Y
Member
I've always used .14 times Hp. But wondered if theres a chart I could get awhole of.

#87346 02/17/04 07:59 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Manufacturer-specific info at www.baldor.com/pdf/brochures/BR435.pdf