I am installing a Buck&Boost transformer. Do i need to have a secondary OCPD.I tried to find it in the 1999 handbook(nec) no luck.

When does an installation require secondary protection?

Merci
Edward.


Thanks
Edward
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2003
Posts: 1,374
R
Moderator
You will probably only have to supply overcurrent protection on the primary side. 450.6(A) and (B) discuss a couple of instances in which secondary OCPD's are required. [Linked Image]


Ryan Jackson,
Salt Lake City
Joined: Jan 2003
Posts: 4,391
I
Moderator
Buck Boosts are autotransformer's and are only required to have primary protection.

450-4(a) 1999 or 2002


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Apr 2002
Posts: 2,527
B
Moderator
They're covered in 99NEC 450-4(a) Autotransformers… Secondary overcurrent protection is generally not required, but also note when “secondary” [shunt] OCP is prohibited.




[This message has been edited by Bjarney (edited 02-09-2004).]