can anyone tell me if they think that a rec. installed for a dishwasher that has a cord can be installed behind the appliance.would this be an accessible location?
|
|
|
|
Joined: Feb 2003
Posts: 687
Member
|
We allways just run the cord to the sink cabnet next to the dishwasher.
During rough we put a box in the sink base wall with a few extentions on it to get thru the drywall and cabnet. Then we can wip off the extension for a disposial, air switch hot/cold water dispencer, and or dishwasher. Then it is covered with a switch garvin for the dishwasher disconect. If the dishwasher has a plug then we use a single receptical garvin so the plug is the disconect.
The nice thing about this way is you can easily addapt to what ever they give you or add at the end.
|
|
|
|
Joined: Jan 2004
Posts: 16
OP
Member
|
my problem is that the dw is not next to the sink base. there is a corner cabinet next to it and the sink base is on a penninsula.
|
|
|
|
Joined: Jan 2002
Posts: 163
Member
|
(1999) 422-16(b)(2)(d) "The receptacle shall be located in the space occupied by the appliance or adjacent thereto."
Dishwashers are considered 'accessible' since you can remove 2 screws and pull them out of the cabinet space.
422-16(b)(2)lists 5 conditions that have to be met where built-in dishwashers are cord- and plug-connected (a,b,c,d, & e).
|
|
|
|
Joined: Jan 2004
Posts: 16
OP
Member
|
i would consider it accessible to, but my local inspector thinks that if you have to disco the water line to the dw to remove it,that its no longer accessible
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
jmc,
I think if a Dishwasher is installed right it should be able to be pulled out of the cabinet without disconnecting anything.
Bill
Bill
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
JMC tell the inspector to read the code article. It is clear the receptacle can be behind the dishwasher. There is no mention of water lines.
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
I agree with both Dave and Scott. The NEC is quite clear in 422.16(B)(2)
Pierre
Pierre Belarge
|
|
|
|
Joined: Jan 2004
Posts: 16
OP
Member
|
thanks for the input, i think i/we/you convinced him
|
|
|