Member
If an outdoor residential spa has a built in GFI, does it need a GFI breaker at the Panel feeding it? Does it need a disconnect near the spa when the panel is not in with site?


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#86935 12/24/03 12:46 PM
Joined: Dec 2003
Posts: 18
D
Member
according to 680-40 for outdoor spas it sends you to 680 parts A and B. 680-12 states that a disconnecting means shall be provided and accessible within sight of all pools, spas, and hot tubs and shall be at least 5 feet from the wall. As for the gfi requirement, in my area a gfci breaker is required but I cant find the article. I dont know if this is a local thing or in the nec. hope this helps.

#86936 12/24/03 12:56 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Yeah, I couldn't find the GFI requirement either. Thanks for your help.


The Golden Rule - "The man with the gold makes the rule"
#86937 12/24/03 01:54 PM
Joined: Dec 2003
Posts: 751
E
Member
Check out 680.44. If I'm not mistaken, a listed spa package with integral GFCI protection is permitted without GFCI protection on the branch circuit or the outlet serving the spa.


Earl
#86938 12/24/03 02:26 PM
Joined: Oct 2000
Posts: 5,392
S
Member
the disco is something that needs to be within sight of the motor, as some tub motors are not intergral to the tub ( as in commercial settings) an E-stop for the serving motor is to be placed within sight of the tub. (from the hip, this might be 680.41)

isn't it interesting that , a permanent hardwired pool should not require a GFI , where most hot tubs & spas are listed for them?

must be something to do with the bonding eh?

~S~

#86939 12/24/03 02:30 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Yep, you would think an in-ground pool would need a GFI for the pump motor. The pool light has one.